Edjack raises an excellent point regards ambient air-water vapour properties. Such psychrometric data is required to calculate cooling effect across an A/C evaporator. An especially significant factor is relative humidity.
In even moderate conditions 1/3 or so of cooling BTUs are used to condense water vapour rather than reduce temperature; in extremely humid conditions well over 50% goes to condensing. Therefore A/C system operating parameters are always stated in terms of ambient temperature and relative humidity. Descriptions such as "my A/C is 41F at 90F ambient" is incomplete and useless for comparison or diagnosis.
If you're interested, a simplified explanation follows.
The A/C can be thought of as performing three functions on the air being cooled as it flows through the evaporator:
1) reducing the temperature of the ambient air-water vapour mixture to the dew point
2) condensing water vapour to liquid at constant temperature at whatever the dew point of the ambient air happens to be
3) further reducing the temperature of the air-water vapour mixture while also condensing out more water vapour as the temperature is reduced.
In moderate ambient conditions the A/C actually operates at only a fraction of its design capacity in order to cool air to ~4C. (4C is the regulated minimum temp to avoid icing the evaporator and blocking air flow to the cabin.) As humidity &/or ambient temp increase, the A/C expansion valve in the evaporator automatically increases the R134a flow rate to provide more BTU/hr cooling to condense more water while striving to maintain 4C output.
But then as the evaporator increases the R134a flow rate to generate more BTU/hr of cooling, the condenser has less less time to cool a unit of R134a. Temperature & therefore pressures (which move in lockstep) increase.
Further, an A/C system's maximum cooling capacity (BTU/hr) is controlled by:
1) RPM, i.e. R134a flow rate varies with RPM
2) ambient air flow rate and temp over the condenser, i.e. removing heat from the compressed R134a. Air flow at testing conditions should be fixed by fans. Higher ambient reduces heat removed from condenser => higher R134a pressure
3) air flow rate through the evaporator. Slower means more time for the evaporator to condense and cool a unit of incoming air-water vapour.
So, at some point the cooling draw at the evaporator equals the heat rejection in the condenser; both are affected by ambient temp and humidity. Net result is that ambient temp and humidity determine A/C R134a pressures (both high & low sides) and output air temperature. RPM also affects cooling capacity, of course. In extreme conditions maximum cooling capacity of a perfectly good A/C can be reached and the air coming off the evaporator rises well above 4C &/or R134a pressures can reach a maximum cut-off point.
Therefore a complete table or graph of A/C performance parameters will always specify: ambient temp, ambient RH, RPM, HVAC fan speed and A/C outlet air temp. Function of the auxillary fan in front of the condenser should be verified too. All measurements are required to determine whether a particular system is OK; one, two, three or four are not enough.